Scott: I agree on the not setting up/breaking down. Heck, I sit on the back step and forego the chair - that's too much of a commitment
Are your batteries made by Windy Nation? If so, then doing what they say is a good idea. If not, I'd recommend seeing what the battery mfgr. recommends. In my case, with Lifeline AGM batteries, there are times they recommend equalizing (which they call "conditioning"). Not something I do often, but definitely in the arsenal.danesk wrote: July 25th, 2020, 6:50 am My charge controller from Renogy seems very adequate, programmable to set voltage boost, absorption and float values...equalization values also, but Windy Nation says do not use equalization for these AGM batteries. I will program the controller to Windy Nation recommendations.
You absolutely, 100% want to install that remote temp comp with any lead acid batteries (which includes AGM). That is used EVERY DAY to deliver the correct voltage to the batteries in the absorption charge stage. Very important. I'll give you an example from my setup: First of all, I have the "best" situation in that my batteries are under the couch (not outside where temps vary more) and the solar controller is literally 3/4" away on the other side of a battery box board. Closest possible temperature situation. BUT, those batteries are a large mass. The underneath of my couch area is not 72º all night, especially in cooler weather. So very often when I'm in absorb (say around 10 a.m.), the controller will show that it is at 75º, and the batteries (at the end of the temp comp probe) will be at 55º. Now imagine the difference if your batteries are outside and the controller inside!danesk wrote: July 25th, 2020, 6:50 amThe controller did arrive with a temperature sensing unit, but I did not install it...would have had to drill another hole in the floor and try to route the very thin wire. Not sure if this is necessary if I'm not allowing a high voltage equalization charge, but will research this more. Worse case scenario is removing that pillar etc. and trying to fish the delicate connector through.
The deal is that the batteries want, let's say 14.4 volts in absorb. BUT, that is at 77ºF. Every degree lower that the batteries are from that, they want more voltage to be the equivalent of 14.4 at 77ºF. Any amount above 77º and they want less voltage to be the equivalent.
So with no temp comp you buy the panels, do a good install, take care to avoid voltage drop in the wiring, buy a good MPPT controller, and then kind of throw it all away because without on-battery temp comp your voltages will only be correct when both the controller and the batteries are at 77ºF. I bet that happens once in a blue moon.
In short, absolutely mount the on-battery temp comp! Also, find out what the actual battery mfgr. wants for charge voltages and durations, and go with that. If your battery mfgr is light on information, and you want to know more, have a look at Lifeline's free "battery manual" which explains it all in detail, in an easy to understand manual. While the exact voltage numbers another company wants might be slightly different, the principles are the same. Knowledge is power (literally in this case
Cool that you have got it up and running! I you want to share any photos, I know we'd all enjoy them.
PS: Good on you with the pillar!