Jon:
I would advise you not to change the voltage cut off from the factory. It is a pain to recalibrate, and it should be a reasonable setting unless you have some unusual setup or configuration.
I have the following table from the previous page:
voltage related to ground when OFF:
V-in 12.47 (12.47 ON)
Sense 12.47 (12.47 ON)
O/R 5.23 (10.09 ON)
alarm 1.07 (0.32 ON)
V-out 0.00 (12.47 ON)
What I should have done is that on the alarm post, I should measure it relative *not* to the ground, but to the V-out because there is a diode or similar component in there. It functions as a ground for the buzzer and the warning LED.
1, Disconnect the gray wire from the LVD so the alarm post is bare.
2, Switch the overhead panel to ON, the LVD should connect if the SENSE wire is good. The green LED ("In use, charging") should be on. There should be 12V between the ground (white wire post) and the V-out. When you measure the alarm post with the black probe of the voltmeter, and put the red probe on the V-out, you should not see much voltage, close to zero. This test to make sure the LVD will turn on when you switch ON.
3, Switch the overhead panel to STORE, the green LED will goes out, and the red LED on the LVD (set point indicator) should be ON. There should be no voltage between ground and the V-out, because you disconnect the batteries with the LVD. If you touch the probes on the alarm post and the V-out again, there is no flow. This test the LVD to shut off when you switch to STORE.
4, Turn the panel switch back to ON. Disconnect your SENSE wire, so that the LVD thinks that your batteries are dead (you don't need to use a long wire to simulate voltage drop, or have to run down your battery on purpose, just disconnect it.) Make sure you cap off the bare wire since if you let it fall and touch the metal frame or the propane line, it will give you a nice spark and set off the 15 A breaker. I would cap it with a wire nut or electrical tape. Anyway, as soon as you disconnect the SENSE wire, the LVD will light up the red set point LED, and you will have 1 minutes to do the following before the LVD cuts off the V-out. Measure the potential between the alarm post and the V-out, you should see 12 V. If you measure the ground (white) and the V-out, you also should see 12 V. After a minute, the voltage on the V-out will be cut by the LVD, and so will be the voltage between the alarm and the V-out. In practice, when the battery got low in the middle of the night, you will hear the alarm buzz for a minute, and then it stops. This test to make sure the LVD will alarms you for a minute when voltage is drop below the set point (simulated by disconnect the SENSE wire).
5, Reconnect the SENSE wire, and turn the panel switch back to STORE. The LED on the setpoint should be lit. The V-out should be off, verify by voltage 0 between the V-out and the ground. The alarm should be off, verify by V-out and the alarm post. Turn your converter on by plug your rig to shore power. You should see the V-out and the ground (white) have ~13+ volt from the converter. Now, here is the important part. Measure the voltage between the alarm post and the V-out, you should see 13+ v there too, since the alarm post is acting as a ground. This test to make sure your LVD is grounding the alarm post and cause the buzzer to sound to alert you to connect the battery if the genset or the shore power is available.
Let us know how your LVD did when you do the procedure above.
Here is the updated table:
voltage with buzzer and warning light on the overhead panel disconnected (gray wire).
ground (white) vs. V-in 12.47 OFF (12.47 ON)
ground (white) vs. Sense (red) 12.47 OFF (12.47 ON)
ground (white) vs. O/R 5.23 OFF (10.09 ON)
V-out vs alarm (gray) 12.47 OFF* (0.00 ON) <----- *V-out only going to be on for ~ 1minute if the SENSE wire got disconnected, unless the converter is on.
ground (white) vs. V-out 0.00 OFF (12.47 ON)